Multiplus II spring loaded AC terminal accept #10 solid?

The "AC in" romex that the RV manufacturer used is #6 three stranded with a #10 solid ground. Can I insert the solid #10 in the ground terminal and expect it to be a secure fit?

Could I fold the #10 over and insert?

If not... what could I do to use the existing romex that has the #10.??

terminals
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
kevgermany avatar image
kevgermany answered ·

You're not supposed to use solid cables in mobile applications. Use a multistrand preferably with a ferrule to terminate.