question

esteban-moreno avatar image
esteban-moreno asked

Absorption to Float triggered at 40% or 60% of SoC (Multi + BMS + VE Smart Lithium LiFePo4 300ah Battery)

Multiplus is going from ABSORPTION to FLOAT charging state when the SoC is at 40% o 60%, which should actually been triggered when the battery is fully charge, if I'm not wrong.

1641564435325.png

Multiplus settings are the recommended ones for Lithium batteries. So floating is at 13.5v and absorption is at 14.2v.

1641564806774.png

1641564855094.png

- Could it be the Absorption time?


Any help would be really appreciate!!! thanks in advance to this great community.

Lithium Batteryfloat
1641564435325.png (78.2 KiB)
1641564806774.png (95.7 KiB)
1641564855094.png (76.4 KiB)
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

esteban-moreno avatar image esteban-moreno commented ·

1641566997730.png

Adding the lapsus between the different charging states from today! It should be 1Hr of absorption and the 1hr of interval until the next absorption, right? thanks.

0 Likes 0 ·
1641566997730.png (21.7 KiB)
klim8skeptic avatar image klim8skeptic ♦ esteban-moreno commented ·
Why are you not using the Smart Shunt as the battery Soc meter?
0 Likes 0 ·
esteban-moreno avatar image esteban-moreno klim8skeptic ♦ commented ·
The smart shunt is in place! it shows 0.01 always, but actually it's passing the information on the advance reports in the VRM. Actually I search why it's showing like that and I did not found an actual explanation. Do you know what could it be?
0 Likes 0 ·
esteban-moreno avatar image esteban-moreno esteban-moreno commented ·

1641576311987.png

Here is the SHUNT information, which is the same SoC that is on the multiplus dashboard!

0 Likes 0 ·
1641576311987.png (25.9 KiB)
Show more comments
1 Answer
rdcat avatar image
rdcat answered ·

Is your smartshunt correctly calibrated / zero'd?
If that voltage is wrong, then all else will be wrong
Multiple adsorbtion is bad for Lithium. less time is better.

If you have DC loads or solar, then the SOC meter (battery monitor) in the Multi should be OFF.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.