What are the correct settings for Lynx BMS setup with 10 Victron 24v batteries?

We installed 10 24v Victron batteries and the Victron dealer did the initial setup. They set the Lynx BMS…settings…total AH 200….batteries 1. Is this correct? Or should it be 2000AH and 10 batteries?

BMS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi @Alec Thyrre , you need to put in the total bank capacity. You are aware that the maximum amount of batteries in parallel is 5? So I assume that is wired in series to be a 48V battery bank - right?

So then its:

- 48V

- 5 x 200Ah = 1000 Ah

- 5 in parallel.


Like this:



c3564c61-a35a-4ac1-a2ff-c78eb5b58347.png


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ commented ·

Ps, also for other people looking for explanation on settings: please check the manual. Its available for download here: https://www.victronenergy.com/dc-distribution-systems/lynx-smart-bms
..

And explains that this setting for the bank capacity, not individual battery module capacity.

0 Likes 0 ·
Alec Thyrre avatar image Alec Thyrre commented ·
First thank you for your reply. We have 3 distributors with each battery on its own spot ie. 2 distributors with 4 batteries each and one distributor with 2 batteries going into a Lynx BMS

According to our dealer that was how Victron said to set it up