question

rocketmanmonaco avatar image
rocketmanmonaco asked

Multiplus low temperature cutoff

Hello,

On my MotorHome, I have:

Smartshunt (w/ temp cable)

A couple of Smart Mppt’s

CCGX (DVCC turned on)

Multiplus 12/3000 (set to Lithium batteries)

My concern is low temperature charging, the mppt’s are not charging below 41F (my setting), I have verified that.
I am trying to verify if the Multiplus will or won’t charge at 32F or 0C. I seem to find all kinds of different opinions.
Do I need some extra wires and assistants to stop charging- I would prefer to not charge below 41F, but I am not sure how to make that happen.

Thanks for your help.

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
snoobler avatar image
snoobler answered ·

1639944830231.png


I would presume the GX shares the smart shunt data with the MP, but I wouldn't take it for granted. Experiment by setting it to a temperature higher than it actually is, and see if the unit will charge.




1639944830231.png (93.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rocketmanmonaco avatar image
rocketmanmonaco answered ·

Thanks snoobler,

I finally found that setting in my iphone app on VictronConnect in the Demo settings.

However, when I connect to my MultiPlus with the MK3-to-USB adapter to make changes to the "charger" setting, There is no "Low Temp cut-off" or even a "temp Compensation" box. I did check the Update software and it says the software is up-to-date.

Does this mean I need the Bluetooth adapter for the Multiplus to change this setting? (And can you have booth the Bluetooth adapter and a VE.Bus cable plugged in and running at the same time?)

Thanks to anyone that can help.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image
snoobler answered ·

To use Victron Connect, you need the bluetooth adapter.


The only way I think I could accomplish it in VEConfigure is through assistants, and that's complicated.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jeffery and Carolyn avatar image Jeffery and Carolyn commented ·

We have a Quattro with after market lithium batteries, CerboGX, and a BMV-712. Can I assume that we can also use the above information to stop the Quattro from charging below a certain temperature?

0 Likes 0 ·
Show more comments
rocketmanmonaco avatar image
rocketmanmonaco answered ·

Just to let anyone else who finds this post know, the Demo Library for the Multiplus was used with a MK3-to-USB adapter and then I used Windows 10 VictronConnect (Not Victron Configure).

Still have not got it all solved yet... but I figured I would help anyone find the correct path.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image
snoobler answered ·

I lost track of this thread. The low-temp charging protection option wasn't added until a recent firmware version. If your firmware is not up to date, you won't have that option.



2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.