Hi. I am looking for the thd figures of inverters and could not see them in the datasheets. Many thanks
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi. I am looking for the thd figures of inverters and could not see them in the datasheets. Many thanks
Hi mcduman,
The harmonics are created by your lines and your loads, not by the inverter, that's why there is nothing in the Victron's datasheet.
Set-up a power line anlyser with THD like this one: https://www.chauvin-arnoux.com/sites/default/files/D00QPA50_4.PDF
That is not true as there is no such thing like perfect pure sine output inverter, hence 0%THD.
The best power inverters are under 3% THD measured on pure resistive load.
Hi Mc. i knew I'd seen them somewhere before, so I went for a look. You're right about them not being in the 'consumer' spec sheets, but seem to be available in the Tech Details section of the relevant model's manual.
< 5% seems to be a common figure, but I did spot one that said < 3%.
thanks for looking. i know < 3% is as good as it gets. however it seems i am unable to locate this spec in the user manual either. there is ac output tolerance which is +/- 3% but this is not what i am looking for.