question

Fra avatar image
Fra asked

Victronenergy Agm deep cycle voltage drop after 7 months

Hello, I repeat a question that I have already asked in a simpler way, because I did not get an answer.

I have a Victronenergy AGm deep cycle 110ah for 7/8 months.
Since November I have noticed a drop in ocv (OPEN CIRCUIT VOLTAGE) of 0.07 / 0.08v for each discharge.

For instance:
Previously with a discharge of - 6ah it had ocv 13.00 / 12.97v,
Now 12.93 / 12.94v.

 before with discharge of - 12ah it had ocv 12.88 / 12.91v
Now it has 12.80 / 12.83v.

Previously with a discharge of - 20ah it had 12.73 / 12.75v ocv.
Now 12.66 / 12.68v.

This decline happened in November. For the first 6 months in the summer, the ocv remained constant.
The battery is recharged every day to 100% with the parameters of the victronenergy datasheet (abs voltage 14.4 / 14.5v, float 13.8v, abs time 1-3 hours, temperature coefficient - 24mV / C °).

The only thing that has changed is the temperature. Before it was on average 27/30 C °.
From November on average it is 20 / 22C °.

For more detailed information on the conditions of use of the battery read here:
https://community.victronenergy.com/questions/111143/victronenergy-agm-deep-cycle-performance-and-boost.html

Is this voltage drop normal? Is it the temperature? Or is the battery sulfating?

Thanks
MPPT ControllersAGM Battery
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Paul B avatar image
Paul B answered ·

A normal full gel ocv is around 12.7 to 12.8 vfor 100% SOC and a temp drop would also affect it a lot as well. the below is a average SOC Voltage chart at 25 deg C


1639060940465.png



1639060940465.png (306.7 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Fra avatar image Fra commented ·
Thank you. My agm victronenergy at 100% was 13.20v ocv after 24 hours unplugged, wehn was new.

Now is 13.10v.

Maybe is temperature. Maybe it stabilize at a slightly lower ocv with use.

I now that the first 2/3 months of use, capacity increase slightly and then stabilize.


Are my battery performance normal for you?

0 Likes 0 ·
snoobler avatar image
snoobler answered ·

Temperature.


Capacity is defined at 25°C. Warmer batteries have more capacity. Colder batteries have less capacity.


-X Ah @ 27/30°C is a different % DoD than at 20/22°C


The -24mV/°C is for charge voltage temperature compensation, i.e., 14.4V is defined at 25°C. At lower temps, absorption voltage needs to be HIGHER than 14.4V to get fully charged. Above 25°C voltage needs to be lower.


Have you programmed your charger with this temperature compensation value?


Example only, not necessarily absolutely accurate:


A 6Ah discharge BELOW 25°C might be 22% DoD while it's 18% DoD at 30°C.


Thus the greater DoD in cold would result in a lower resting voltage.


The smartshunt allows setting a parameter to adjust capacity based on temperature in Misc:


1639064784677.png


My particular FLA batteries are -1.1%/°C, but that varies with manufacturer and type.


1639064784677.png (48.0 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Fra avatar image Fra commented ·

Halló, thanks you. Yes I programmed my mppt charger exactly with datasheet victronenergy parameters.

Abs 14.4v/14.5v. Temp coefficient - 24mv/C. Float 13.8v. Abs time from 1 to 2 hours depending of dod. My average dod is 15/20% daily.

One time per month I make 3 hours abs at 14.6v (a slightly equalization becouse is a vrla battery). Is unnecessary or dangerous?

You say:"X Ah @ 27/30°C is a different % DoD than at 20/22°C"

I agree with you, but I think these not justified a 0.08v drop in ocv.

A loss of 4% of capacity from 30 to 20 C Celsius, is not a 0.08v drop in ocv with same Ah discharge. It would be less.

I'm wrong?

I now all waht you say about cold and internal resistance and capacity drop. Thank you for your reply.

0 Likes 0 ·
snoobler avatar image snoobler Fra commented ·
You are trying to equate OCV to SoC. This is unreliable. You are doing it at different times and different temperatures - this makes it even less reliable.


Are you allowing a full 24 hours of static rest before recording OCV readings? If not, it is even more unreliable.


All evidence points to reduced capacity associated with reduced temperatures and failing to compensate for that.




0 Likes 0 ·