SmartShunt battery bank capacity setting

I have two 12 V 100 Ah SLA batteries that will be connected in parallel (recommended by Will Prowse, https://www.mobile-solarpower.com ) to be monitored by a SmartShunt. Is it correct that I would set the SmartShunt battery capacity setting to 200 Ah? Any comments on my off-grid cabin design are welcome as this is my first solar system install.

smartshunt.jpg


BMV Battery Monitor
smartshunt.jpg (169.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
kevgermany avatar image
kevgermany answered ·

200 correct.

Take the positive load from the left battery.

Wire the charge +ve input to there as well.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jav6joev avatar image jav6joev commented ·

@kevgermany Thanks. The 'charge +ve' is what? the charge controller? I have a DC Fuseblock (with in-line fuse), Pure Sine Inverter (on same in-line fuse) and a Charge controller (with in-line circuit breaker), all going to the same positive terminal?

0 Likes 0 ·
Show more comments
jordan-de-geus avatar image
jordan-de-geus answered ·

Did you find out if the smartshunt is total bank capacity or if it's usable capacity?