question

noel1968 avatar image
noel1968 asked

Clarification on EasySolar 24V, 1600VA

I plan to buy EasySolar 24V, 1600VA. I have a very basic question. After sundown when there is no Solar power generated, will the loads be from the batteries till a certain level of charge in the battery and then switch over to AC power

EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
boekel avatar image
boekel answered ·

Yes you can but you can program it to do as you want to, like keep 50% of the capacity for when grid fails.

Normal behavior for grid connected systems is to keep grid connected, but try to keep grid usage at zero until battery is discharged (to an adjustable level).

8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

noel1968 avatar image noel1968 commented ·

Thank you

So the software which will be provided gives you the option to change the parameters to 50%.

0 Likes 0 ·
Paul B avatar image Paul B noel1968 commented ·

You would need a MK3 to program the easysolar unit and please read the all the manuals and the online help files.


And yes the programs are free from the victron site.


Again we would sugest that you use a experianced tech to do the setup if you have not done it before.

0 Likes 0 ·
Show more comments
a-v avatar image
a-v answered ·

Use "(dedicated) Ignore AC" in the confuguration which fits you more, at the virtual switch. The EasySolar will change to AC in when the batteries go under the preset level. Then you do not need Color Control.

https://www.youtube.com/watch?v=V1Zceq02vMA

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.