Hi,
I currently have a 10KW Fronious 3 phase PV connected in my house, and I'm looking to add a battery bank and 3 x Multiplus 2s.
Although I have about 13.2KW of solar panels, due to the layout on my roof, my PV inverter generated power is always less than 7KW, absolutely never more than 9KW. The layout and quantity of solar panels are configured to provide a lower peak power, across a longer period of the day.
My question is if ok to use 3 x 3KW Multiplus 2 per phase (Total 9KW), rather than 3 x 5KW Multiplus 2s, and still meet the Factor 1 Rule requirement?
From what I can determine, the answer is yes, since the PV power per phase will always be less than 3KW, phases balanced.
Can someone kindly confirm/advise?
Regards