question

greekgeek avatar image
greekgeek asked

solar charger not charging?

My solar charge controller shows zero charging input some cloudy days. Has enyone experienced something similar? is it normal? i have attached two solar charger in my battery each of them providing power from a different string; i have also connected a smart battery sensor that provides data to the chargers. am i doing something wrong here? thanks for your input, cheers

smart solar charging behaviour
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
Perhaps you could share your mppt's history with us?
0 Likes 0 ·
greekgeek avatar image greekgeek klim8skeptic ♦ commented ·
u r right, i will do that asap
0 Likes 0 ·
greekgeek avatar image greekgeek klim8skeptic ♦ commented ·

as you can see, 4 days ago the load output from string 1 (2s2p) is zero while the output from string 2 (1 240w/24v panel) is 50 wh. This was a cloudy day with minimal electricity usage from the system, just a couple of lightbulbs. Both solar controllers are set at the same configuration (battery=>victron 2=>deep discharge).

screenshot-2021-12-04-09-17-37-223-comvictronenerg.jpg

the same thing happened a few days ago

screenshot-2021-12-04-11-42-45-441-comvictronenerg.jpg

screenshot-2021-12-04-11-43-03-764-comvictronenerg.jpg

the first controller is on float mode while the second is still in absorption. Any input is much appreciated, cheers.

0 Likes 0 ·
4 Answers
klim8skeptic avatar image
klim8skeptic answered ·
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

greekgeek avatar image greekgeek commented ·
so you mean to make a network between the two chargers without connecting them to the battery sense?the article provides very few details, cheers
0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ greekgeek commented ·
From what I have read, 2 mppt's will communicate and go into master/slave config.

Plz confirm.

0 Likes 0 ·
greekgeek avatar image greekgeek klim8skeptic ♦ commented ·
first of all thank you for your patience and expertise, i set up the controllers in the manner that you suggested yesterday, i ll check the readings tonight so that a full 24hr has passed. I hope that it will solve the problem.

in my previous setup i set up a network between the smart bat sense and the two controllers. I thought that this is the optimal setup so that both controllers receive data from the sensor. anyway i will let you know.cheers

0 Likes 0 ·
kevgermany avatar image
kevgermany answered ·

Might be worth checking the settings on your controllers as well.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

greekgeek avatar image
greekgeek answered ·

this is getting weird

screenshot-2021-12-07-19-42-19-724-comvictronenerg.jpg

screenshot-2021-12-08-18-50-44-055-comvictronenerg.jpg

the first controller reports a max battery voltage at 14.35v while the second one at 14.45v (i cannot be certain about the min bat reading )

both controllers are set in a network working in tandem



screenshot-2021-12-08-18-50-59-934-comvictronenerg.jpg


each controller has also the same settings

set-1.jpg

set-2.jpg

any input is wellcome.


4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

greekgeek avatar image greekgeek commented ·
i would like to add that the two strings are loacted side by side. Is there a possibility that the voltage differences are attributed to the sun going down on the panels (and similarly going up in the morning)?
0 Likes 0 ·
Show more comments
kevgermany avatar image
kevgermany answered ·

Could be a poor battery connection causing resistance and a voltage drop.

The switch from absorption to float is based on time elapsed. Not sure if this can be different on the two controllers. If it is, it shouldn't be

2 |3000