I have 12v small loads hub (1A usb charger, 5W fan) connected directly to smart battery protect. Inverter is connected directly to battery, it runs refrigerator 24/7 on ECO mode.
Both inverter and battery protect have low voltage cutoff enabled at same value, as to protect battery from over-depletion. Is this correct?
How to wire my setup so i avoid this: (from inverter manual) "Do not use Dynamic Cut-off in an installation that also has other loads connected to the same battery: the battery voltage will drop because of the extra load, but the Dynamic Cut-off algorithm in the Inverter is not aware of that load: hence the Inverter will shut down too early with an under voltage alarm. " ?