Help with first time Off Grid 3 phase

Hi

I am planing an installation with 3 Multiplus 48/5000 off grid in 3 phase. I will like to get an assistance on how to use Ve configure to set up the configuration needed.

This is my first time on such configuration so please be patient with me.

VEConfigure 3
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Paul B avatar image
Paul B answered ·

This would normally be done with the help of a Trained Victron Tech by your dealer. This is highly recommended.

however, we can try and help if you can layout the configuration that you are looking to achieve, and a wiring diagram of the proposed installation would also be helpful.


battery sizes

type of batteries

are you connecting solar and how

what loads are you connecting etc

What size generator is connected





1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mka avatar image mka commented ·

Loads is 8KW

0 Likes 0 ·
boekel avatar image
boekel answered ·

Please start by reading all the manuals, and finding someone experienced with large Victron installations to help with the installation. + check the system diagram by your Victron distributor / installer.

If something in the manuals is unclear, you can ask here for help.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mka avatar image
mka answered ·

thank you for the reply

Battery sizes 12V200AH X 12

types of batteries VRLA

connected to 275W X 27 in 9 string with 3 MPPT 150/45

No generator

For the load I don't have it yet.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

so what kind of a system? grid connected?

I would never advice 12V VRLA batteries for a big system and the total usable capacity is very small (about 15 kWh).

Please read the community guidelines, and please hire a Victron specialist to help you with your system. Do you have experience with single phase Victorn systems?

https://www.victronenergy.com/live/community_guidelines

0 Likes 0 ·
mka avatar image mka boekel ♦ commented ·

I have taken your advice and I have seen a guy who is familiar to this type of installation and he is going to help. I will be posting the results here so I will have your advice too.

1 Like 1 ·
mka avatar image mka mka commented ·

No it is not grid connected. It's an isolated site so it's going to be mainly on solar.

0 Likes 0 ·
boekel avatar image boekel ♦ mka commented ·

Very good. let us know what his advice is.

0 Likes 0 ·
mka avatar image mka boekel ♦ commented ·

yes I do have expériences in single phase victron system

0 Likes 0 ·
Anil Ghatikar avatar image
Anil Ghatikar answered ·

I have an exact same system( with Quattros ) but running in ESS with BYD 10 KWH /10 KW batteries as for off-grid setup you will need 15 KW/50 = 300 Amp ( ignoring efficiencies)capable battery system at C10 rate that is 3000 AH battery bank ( or 6000 AH for C20 rate) anything smaller and your battery bank will require frequent replacement and will not last

e.g. a Panasonic VRLA-SLA LC-P12200 will give 200 AH at C20 but give only 169 AH at C3

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mka avatar image mka commented ·

The load will 7KWH maximum 5 hours daily.

0 Likes 0 ·