question

pda1 avatar image
pda1 asked

Wiring BMV-712 for 24v system?

I need a clear wiring diagram for installation of a BMV-712 (Smart) to a 24v PV system that's using 2- 12v LiFePo batteries in series (Battle Born).

The instructions, while good, aren't clear enough and have me concerned I'll wreck something.

BMV Battery Monitor
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

It is the same as with one 12V battery.
You have one positive (24V) and one negative (0V).
The shunt have to be connected to the negative before it goes to the system.
1637433398930.png


1637433398930.png (61.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image
kevgermany answered ·

Maybe you are overthinking it.

Assume you have the shunt with it.

0V negative of battery goes to the battery side of the shunt.

Load side of shunt goes to common negative for all loads and should be grounded. Also negative of charger.

24V positive of battery goes to fuses etc. Also charger positive.

There are two fused thin red wires . One goes to +24V of the batteries and from there to the left green connector(battery side). The other goes to the +12V midpoint of the batteries if you want mid point monitoring, or to an aux/starter battery and goes in the right green connector.

Then there's a plug in cable to plug into the shunt and the back of the 712.

That's it.

If you want to connect to a GX device such as the CCGX, you need to buy a VE Direct cable, this plugs into the back of the 712 and the GX device. Otherwise the VE direct socket is left unconnected.


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
I see Matthias beate to it as U was typing. Ah well.
0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ kevgermany ♦♦ commented ·
Sorry, hehe. :-)
0 Likes 0 ·
kevgermany avatar image kevgermany ♦♦ Matthias Lange - DE ♦ commented ·
Macht nix
0 Likes 0 ·
pda1 avatar image
pda1 answered ·

Where does the negative output from the Victron MPPT SCC get connected to? Directly to the negative on the battery or on the negative BATTERY terminal on the BMV or the negative LOAD side of the BMV?


Thank you

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·

Except the battery, everything is connected to the "load" side of the shunt.


But you should use busbars. Don't stack multiple wire lugs on a single bolt. Maybe two wire lugs on a bolt, if you must, but not more than two.