2 x Multiplus II, Grid tied, with 32kWh battery, Solar Primo 8.2

Hi there,

Is there any SLD or connection diagrams available for following setup?

Can someone please guide us for our first install with Victron? Any suggestions or tips?

I have attached BOM as well



victron.jpg

1636671147567.png

1636671160634.png

Multiplus-IIcerbo gxFronius
victron.jpg (3.6 MiB)
1636671147567.png (70.9 KiB)
1636671160634.png (19.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Rob Duthie avatar image
Rob Duthie answered ·

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

adaptenergy avatar image adaptenergy commented ·
Hi Rob, Thanks for providing the SLD. This helps a lot. Any tips on Installing and commissioning? especially programming the inverter charger?

Thanks

0 Likes 0 ·
Rob Duthie avatar image
Rob Duthie answered ·

Hi

Make sure all inverters are running the latest firmwares this applies the Fronius units as well.

You can use the VE configure on the phone app to do 2 parallel units OK. You will need to use the PC or laptop to install the ESS assistant as required into both units, this is were you setup charge control, grid control, etc.

Just a Note: you should do some sort of training for parallel systems and how they are wired etc

As it is all critcal to get this wright with the correct cable and cable lenghts for AC and DC very important.

Regards

Rob D