Real world experiences with Multiplus or Phoenix Idle Power Consumption (no load)

Recently I was talking with someone, who seemed to have a pretty strong and emotional bias against Victron and higher end inverters in general, who asserted that Victron Inverters--specifically the Multiplus--exceed the idle consumption listed in the spec sheet by about 50% (~30W for the multiplus 3000/24).

I'm hoping those of you who have bothered to check, can provide some data points. Has the idle consumption you have observed (excluding power save modes), been higher, lower, or spot on, when compared to the datasheet?

MultiPlus Quattro Inverter Chargerinverter current draw
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
iand avatar image
iand answered ·

There have been multiple reports on this forum (a search will find them) of this behaviour for the bigger Multiplus/Quattro inverters, specifically 48/10000 models which are rated at 55W idle in the data sheet but (some of which -- not clear how many) measure around 100W.

Victron said that this was due to unit-to-unit variation and not something that could be fixed for a "high-power" unit, and that customers should "contact their dealer to find a solution" -- though it's not clear what this solution would be.

See here, for example...

https://community.victronenergy.com/questions/92644/quattro-4810000-high-idle-power-consumption.html

https://community.victronenergy.com/questions/6893/no-load-idle-consumption-victron-quattro-481000014.html

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dzl avatar image dzl commented ·

Thanks, I did search and did see a few reports of this with the higher power Quattro units.

But (1) the cases seem limited to higher powered quattro units, I haven't come across mention of similar issues with Multi or Phoenix units, and (2) what gets volunteered/reported will tend to be negative or out of the ordinary experiences, and probably not reflective of the norm. By asking, I'm hoping to get answers from a more representative cross section of people, than would take the time to post about it on their own.

0 Likes 0 ·
Show more comments
shaneyake avatar image
shaneyake answered ·

From my experience using Multiplus-II 48/5000/70-50 230V
Idle is around 20W +-5W, bounces around a little.
Low load like 80-100W, the inverter will around 60W itself.

I have installed quite a few 48/5000 and have never seen close to the 100W+ some people are reporting.

This is measured by the Battery BMS which is probably only +-10W accurate.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

iand avatar image iand commented ·
The 100W was for the Quattro 48/10000 (80W for the 48/8000), so would expect maybe 60W for a "bad" 48/5000 compared to zero-load spec of 35W. Multiplus II zero-load power is specified as 18W/29W/38W for 5000/8000/10000, so your 20W agrees with this.
0 Likes 0 ·
rslifkin avatar image
rslifkin answered ·

My Multiplus Compact 12/2000/80-50 120v is right around 9 - 10 watts at idle with no load. Spec is 9 watts, so I'd say it's close enough.