I am still in the planning phase and would like to install 3 Mulitplus2 48/5000 units.
Is it possible via Modbus TCP or the remote contact on the devices to switch off the inverters for phase L2 and L3 and keep L1 running?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I am still in the planning phase and would like to install 3 Mulitplus2 48/5000 units.
Is it possible via Modbus TCP or the remote contact on the devices to switch off the inverters for phase L2 and L3 and keep L1 running?
Basically No. The three phase set of inverters will throw an error if one or two of them are shut down.