Current limit and power assist with ess

with ess and all the loads in AC / IN in a multiplus II with cerbo, can it be configured so that in case of going over the contracted network power the inverter stops consuming (if it is charging the battery) and goes on to inject energy from the battery to the network input and thus avoid jumping the icp??

ESSpowerassist
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

Adjust the AC shore power limit to the same level or lower than breaker and you should be fine. this will automatically reduce the charging or draw from the batteries instead of over loading the breaker