wiring question for smart shunt

Hi, I have a smart shunt in my camping solar system. I have bought an A/C charger from Victron as well and want to hard wire it into my system. My question is on the ground do I go direct to the battery negative or do I go downstream of the shunt like all my other ground connections. The confusion for me is all electric users are downstream but this is a supplier so does it matter if it is upstream or downstream of the smart shunt?

SmartShunt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
kevgermany avatar image
kevgermany answered ·

If you bypass the shunt with the charger negative, you'll never see the battery charging. Like all the other negatives it goes through the shunt to the battery.