What happens with two Multiplus in parallel not linked with each other

Background: I have an old Multiplus 48/5000/70 and I would like to increase the available power with a second battery bank

I'd like to know what happens if I connect the output of a Multiplus to an existing grid formed by another Multiplus. Would it be any different if any or both of the Multiplus is a Multiplus II instead. note that in this example the two Multiplus would not be linked together in parallel, it cannot work as this would require a single battery bank.

Take this schema from the MultiGrid datasheet.

1635441890321.png

In this schema, Let's replace the MultiGrid by a Multiplus II (as I understand the Multiplus II is an improvement of the MultiGrid). Let's replace the PV inverter by another Multiplus and the PV array by a separate battery bank (that too has solar panels).

What would happen in such a scenario ?

edit: an answer below tells us that it's impossible to connect the output of two Multiplus together without linking them. But then, if the Multiplus is capable of feeding back current to its AC input, the second Multiplus can be connected via its AC input.

If it doesn't work by replacing the PV Inverter by a Multiplus, can I take the PV inverter and plug it to some batteries instead ?

Thank you

Multiplus-IImultigridgrid parallel
1635441890321.png (32.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
shaneyake avatar image
shaneyake answered ·

You can not link the multiplus outputs without them being in parallel.
Based on your other post, you are trying to use another battery bank that you already have.
It is possible to have them in series but might not be worth the work to get working 100%
You can just have the second unit run until battery low and never push back to main inverter to make things simple.
I have a micro-grid running like you would want. Here is my blog post about it.
https://shaneyake.blogspot.com/2021/09/micro-grid.html

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image
Kevin Windrem answered ·

You can not connect the outputs of two Multi inverters together unless they are programmed to work in parallel and linked with a VE.Bus cable. Victron requires the units to be the same model and version and run the same firmware. In addition, proper load sharing requires equal length cables.

PV inverters are designed to tie (connect in parallel) to a grid which includes the output of a Multi. As far as connecting batteries to the solar input to the PV inverter, you'd need to consult with the inverter manufacturer. You'd need to find a way to charge the batteries.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tcircuns avatar image
tcircuns answered ·

Hi Shaneyake,

I'm going to install my first Multiplus II 48/5000. I've been looking for options on adding a new one in a future, but maybe using different batteries.

After reading your blog, in my case I was thinking on a simplified version of your one, as I was only thinking on using frequency shifting from master inverter to control exported power of slave one (connected in grid-parallel).

That should be giving me the sum of power of both Multi and the posibility to have both fully controlled by master one.

I am not sure if that's possible, but when I read your post, specially next paragraph, I thought that is possible:

  1. "Other Grid code, may need to be set on the inverter to allow frequency shifting of the master to work correctly. I have slave GX monitoring input frequency so that if the Master shifts the frequency the slave will reduce it's export to the Microgrid and eventually disconnect. This is to prevent the master inverter and battery from getting overcharged or overloaded, This is only used if comms failure or to control Enphase system. You also need to disable Overvoltage feed-in via Modbus on the slaves if the grid is lost. This allows more control over export when batteries are full or close to full."

There I understood what I was thinking about is possible, but I'd like more details about that.

- Is that a control I could implement on slave Multi using NodeRed?

- Is that GX NodeRed firmware an standard Victron one anyone could install and use?

- Could that work fine as the unique master/slave configuration?

- Maybe I should set a maximum power export limit, in order to not sending too much power to master Multi.

Does that makes sense?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

home3131 avatar image
home3131 answered ·

I understand this is a old issue. But what happens when I have the same situation with 2 identical setups ( cerbo's, multiples, bms, shunt, etc ) one on L1 and the other on L2 of the grid distribution box. would that work ( I cannot connect the multipluses or cerbo's

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources