Hello
I have a 7.8 kWp solar system with a Fronius Symo 6-0-3-M inverter and a Varta Element 6 battery.
I want to add backup power capability to the system for cases of power grid failures.
The inverter is 3-phase coupled to the house and I want to provide backup power to the entire house on all three phases, within the limits of 16A per phase (230V). In addition there will be a diesel power generator (8KVA) as well, which shall be integrated. As battery I would consider a BYB LVS 12.0 kWh system for start.
Even after reading lots of information about Victron and possible configurations I still have a ton of questions. I hope somebody here is kind enough to help me through the thought process.
- If I want to supply all three phases with backup power, I have to have 3 Victron units?
- Can I use 1 Quattro for the generator to come into play on one phase (L1 e.g.) and for the other two phases use a multiplus?
- Will all three Victron units be conencted to the same battery stack via some master charge bus?
- If I keep the Fronius it would be AC coupled and deliver up to 6000W PV power, how does that affect the dimensionig of the Victrons? 3x3000 = 9000 (okay?) or each all units have to be capable of handling the full 6000W?
- I have an additional 5000W UPS for the most critical loads, so for this phase I would disable the Victron embedded UPS?
Thanks in advance :)