question

colin-foster avatar image
colin-foster asked

ESS Multiplus-II not inverting

New install

Multiplus-II 24/3000/70-32
Product ID 2611
Firmware 466

Colour Control
Firmware v2.73
Build date 20210830194024

PV Inverter connected on Multi Output 1
Aurora Uno
Coupled to Multi via Victron AC current sensor
on aux 1
power readings on both PV inverter and Multi match

Battery 400 Ah
100% SoC


System setup
ESS
AC1 input GRID
Monitor for Grid fail ENABLED
Battery monitor AUTOMATIC
Mutli on VE Bus
DC system NO
Battery Monitor Multi VISABLE

DVCC OFF

VRM ENABLED

ESS
Optimized (with BatteryLife)
Grid metering INVERTER/CHAGER
Multiphase regulation INDIVIDUAL PHASE
Minimum SoC (unless grid fails) 20%
Active SoC 45%
Battery Life SELF-CONSUMPTION
Limit Charge power OFF
Limit Inverter power 1500 Watts
Grid setpoint 50 Watts
Grid feedin ENABLED
Scheduled charging DISABLED


PROBLEM
system does not go into Inverter mode at any time.

TEST
Grid fail Inverter came on as expected.

NOTE
I have read that the problem is with firmware v466
and that I should revert to v465. Can anyone confirm this
and if so point in the right direction to do it.

Thanks for any advise.


Multiplus-IIESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
shaneyake avatar image
shaneyake answered ·

Please update to the latest firmware which is 487.

Just a quick question is the power switch in inverter mode or charger only?

Has the inverter been setup using VE. Configure? Is all your ESS settings correct in the assistant?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

colin-foster avatar image
colin-foster answered ·

Thanks shaneyake,

After posting yesterday and more reading I realized that although the system tells me it has the latest firemware there are in fact later versions. I have downloaded v487 and will update asap.

Switch is in inverter.

System was setup with VE configure, ess & current sensor assistance installed and setup.

Thanks for your help. I expect the firmware upgrade will sort the problem.

Colin

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.