Start airconditioning system automatically

I would like to switch an air conditioning system automatically. The rules are simple:
If the SOC> 98% it should start and if the SOC <60% it should stop and it shoul stop also if another system uses 1000W.

So the rule is exactly the opposite of the generator rule. Unfortunately, this cannot be inverted. You could use a switching relay that inverts the generator circuit?

How would you solve that?

Generatoraircondition
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

harold avatar image harold commented ·
Look to the use of Assistants, to be programmed in your MultiPlus or Quattro
0 Likes 0 ·
1 Answer
Mark avatar image
Mark answered ·

What Venus device do you have? If you have a CerboGX or VenusGX then the relay has NO & NC contacts, you can achieve what you want by simply using the NC contacts.

But if you want complete control consider using Venus OS large image with Node-RED https://www.victronenergy.com/live/venus-os:large, it is still in beta phase/not officially released but working very well for some time now. Note that Venus OS large image / Node-RED is not officially supported and may require some time to be invested if it is totally new to you.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic

Additional resources still need to be added for this topic

MultiPlus Generator FAQ

GX - Generator auto start/stop

Automatic Generator start/stop

 Hybrid Generators

Virtual switch - Generator start/stop