Autotransformer output voltage different

I just purchased a 100A Autotransformer, with 240V input from a generator and expecting two equal split phase outputs. Below are my readings (5v difference)

Unloaded

Generator output 235VAC

L1-N is 115VAC

L2-N is 120VAC

Loaded ~226VAC

~110

~116


I have swapped my loads on the output and no help. Also removed PE coming from generator to remove any question of N/PE bonding in the home electrical panel. I see other posts where differences were noticed but none connected to 240 on the input. I can only explain this by the center tap of the transformer is not accurately placed. Any ideas? I have started RMA process.


Autotransformer
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

shaneyake avatar image shaneyake commented ·
Can you explain why this is a problem?
0 Likes 0 ·
1 Answer
Mike Dorsett avatar image
Mike Dorsett answered ·

difference is less than 5%, so this should not be an issue.