question

benb avatar image
benb asked

ET112 - fuse requirements?

Hello,

In the manual, it's mentioned to put a fuse on the neutral wire when connecting the ET112 (https://www.victronenergy.com/live/energy-meters:et112), but it doesn't state what type of fuse?
There's not much information to be found. A manual from Carlo Gavazzi makes it look like this is optional (https://gavazziautomation.com/images/PIM/DATASHEET/ENG/ET112_DS_ENG.PDF), but it's not clear at all.

Energy Meter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
markus avatar image
markus answered ·

This is a screenshot from the manual you posted:
01eb7864-f384-4130-abff-8c479405fa44.jpeg
BR


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

markus avatar image markus ♦♦ commented ·

The manual states regarding that fuse:

„If required by local law“ This is from a 3 phase meter manual, but it will be the same for the 1 phase meter. So it seems you have to ask your lawyer about this fuse ;o)

a4068411-de00-421d-877a-3dacf9592a97.jpeg