question

manjo avatar image
manjo asked

Cerbo GX control intellitec 12v pump control.

I want to be able to switch on/off manually a 12v water pump controller. Intellitec 0000145100 10 Amp Monoplex Water Pump Control https://www.amazon.com/dp/B00A2TBL7A. Are rhere any reference wiring diagram I can use to use relay 1 or 2 to function as a switch for the pump controller?

cerbo gxRelaywiring diagram
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@manjo

At present only Relay 1 is available for use via programming. Relay 2 is only available via manual operation from the Relay menu on the GX.

https://www.victronenergy.com/live/venus-os:start#comparison_table you can use whatever pump control matches the capabilities of the relay. So it is usually used to signal another contactor to switch the load on or off. NO -normally open and NC normally closed you wire those two depending on how you need the unit to operate.

DC up to 30VDC: 6A
DC up to 70VDC: 1A
AC: 6A, 125VAC

So if you need the relay to close to switch on the pump you use the NO side of the plug for the relay. and two wires normally.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.