100/20 charge controller at 48V

Hello, is it right that the 100/20 charge control only outputs 1A when using a 48V system?

I dont really see the point in a 1A output! Its also kind of mis-leading as its rated at 20A.


Please confirm.


Thanks

charge current limit
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
JohnC avatar image
JohnC answered ·

Hi @James Morrison

The 1A is the output of the LOAD terminals, not the charge terminals. Very few people have 48V direct loads, it's mostly to feed an inverter, and they're not recommended on the Load terminals anyway. But that 1A can be used to throw a relay to protect the batts from overdischarge. A feature rather than a failing, all of the larger 48V units have no Load terminals at all..

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

james-morrison avatar image
james-morrison answered ·

Okay, thats makes more sense. Thank you for the quick reply, very helpful.