I have been running a Victron Microgrid with Multiple independent systems as a Test for a larger system. Has anyone else done anything similar?

system.png

More Info: https://shaneyake.blogspot.com/2021/09/micro-grid.html

microgrid
system.png (88.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
swebbweb avatar image
swebbweb answered ·

This is very interesting, I've been considering the Idea of running multiple ESS on an islanded microgrid but am unsure how stable it would be. Don't have the means to investing in two more multiplusses and batteries to find out!

I've made a control algorithm to instruct each ESS shown below to help balance the grid and storage.


chargingess1full.png


chargingess1full.png (138.5 KiB)
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

shaneyake avatar image shaneyake commented ·
Yeah, it isn't that difficult till the Main system has SOC of 100% and you need to throttle down the export of the other units. That is the hardest part to get stable.
0 Likes 0 ·
swebbweb avatar image swebbweb shaneyake commented ·
Okay nice that's encouraging, I'm thinking the main grid would be better using ultra capacitors and kept at 50% instead of providing any significant storage. I'm a fan of load banks to dump any excess when the ESSes are full.
0 Likes 0 ·
shaneyake avatar image shaneyake swebbweb commented ·

You don't actually need to do that. I have implemented this with regular LFP at the master, you just don't bring it all the way to 100%, like 95% works fine.
But I do have communication between all the nodes, so the master can set export limits for the slave nodes in realtime. There is a way to do it with frequency shifting but I haven't been able to tune that to be perfectly stable.

0 Likes 0 ·
swebbweb avatar image swebbweb shaneyake commented ·
Have you experienced issues with cell balancing doing it this way? I'd imagine the grid battery would start to get unbalanced if it can't get to 100% or risk cell overvoltage close to 95%. This is why supercaps would be a more maintainable solution in my view.
0 Likes 0 ·
Mike Dorsett avatar image
Mike Dorsett answered ·

The only issue with this type of system is that the grid forming node - the master system MUST have a power equal to that of the permitted reverse power of all the other nodes combined. This is needed to follow Victrons 1:1 rule for ac coupled systems. Given that restraint, there is no reason why this should not be made to work.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

shaneyake avatar image shaneyake commented ·
You actually don't have to follow the 1:1 rule. You just have to be able to handle the peak output for a few seconds till you can ramp down the nodes.


The master node has to be bigger than any of the slave nodes but does not need to be equal to all slave nodes. I have tested this and it is stable.

1 Like 1 ·