question

behl avatar image
behl asked

EM24 and ET112 on same USB Dongle

I have a EM24 on the USB Dongle and it workes fine. Then i added a ET112 (and changed the Modbus ID of the EM24 from 1 to 2 as described in the manual).

Now no Meter is recognised. If i disconnect one meter (EM24 or ET112) the other one works fine. So both meters are OK (and the cable too).

What can i do?

Multiplus-IIem24rs485
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

behl avatar image behl commented ·
If i disconnect the GND connection between EM24 and USB Dongle then both energy meters work fine!

So there is no problem with the Modbus addresses

But the question is: should i regular connect the GND between the energy meters and the USB Dongle?

My configuration:

EM24 ----7m cat7 cable ---- USB adapter ---- 8m cat7 cable ----ET112

No termination, two twisted cables for A and B, another cable for GND

0 Likes 0 ·
Show more comments
2 Answers
Rob Duthie avatar image
Rob Duthie answered ·

Hi

You need to change the ID address using the the CaloGavzz software not the Venus software.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

behl avatar image behl commented ·

I changend the ID directly on the Energy Meter - as described in the Victron Energy Meter EM24 RS485 manual.

0 Likes 0 ·
Rob Duthie avatar image Rob Duthie behl commented ·
Need to force it using the Carlo Gavazzi software that is how i have done using 2x meters on one cable and it works.
0 Likes 0 ·
marcopagano avatar image marcopagano Rob Duthie commented ·

I changed the IDs in Carlo Gavazzi Software and the Meters are correctly recognized, but the ET340 gets sometimes lost without any reason :(

Is the cable maybe too long. I used the original 5m one without any extension. Only cut it to passtrough to the second meter.

0 Likes 0 ·
l81ker avatar image
l81ker answered ·

the GX device addressing is limited. You have two choices, simple = run two separate RS485 cables. or more complicated change the device modbus address, but set them as discussed above on the actual meter using the Gavazzi software. Install it on a laptop, plug the USB RS485 cable into the laptop, change the address of 1. You must temporarily disconnect the one meter while you programme the other. I found it here. Page is Norwegian but programme runs in English https://www.gavazzi.no/nedlasting/software/software-ucs/

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic

Energy Meter Manual EM24 RS485

MultiPlus-II Product page 

MultiPlus-II Manual

Multiplus-II GX Online Manual

MultiPlus-II 230V Datasheet 

VE.Bus Error codes

Additional resources still need to be added for this topic