question

bloudan avatar image
bloudan asked

Float voltage is too high when ac charger on

When batteries in float,

Float voltage goes to 30v when ac charger turns on. Easysolar 24/1600.

Without ac charger from pv only it is around 27.30v which is were it suppose to be. What could be causing the wrong reading every thing is in default settings.

EasySolar All-in-One
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@Bloudan

They do both need to be programmed for your batteries.

0 Likes 0 ·
Show more comments
1 Answer
Paul B avatar image
Paul B answered ·

Suspect that your AC charger has a problem and its overcharging so you need to check its setting and make sure they are correct in the unit. Or maybe the easysolars Inverter/chargers Reference voltage wire is incorrectly connected

2 |3000