Multiplus Compact 12/2000/50 Fuse Type not specified

Looking at the manual for this unit under section 4.2, we don't see recommended fuse type. Given surge current, inverter efficiency loss, and true wattage, we were going to use a Class-T fuse. Why has Victron not suggested a specific fuse type? Especially one with a higher AIC. What fuse type have others used?

Thank you.

Multiplus-IIfusesinverter current draw
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

For the DC fuses, suggested types are MIDI, MEGA or ANL:
https://www.victronenergy.com/upload/documents/Datasheet-Midi,-Mega-and-ANL-fuses,-and-fuse-holders-EN.pdf

Other fuse types which exceed the parameters of the suggested fuses could also be used.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ve-user avatar image ve-user commented ·
Too bad that chart doesn't include AIC. We've got an app for that... Thanks for your response.