mercman avatar image
mercman asked

smart Shunt

I hope this is not a silly question to ask but I have 3 x 12v batteries wired in parrallel ( + to + & - to - ) where my multi-plus inverter has two positive leads & two negitive leads coming off two batteries. When I install my smart shunt ( If correct ) I put the two negitive leads coming back from the inverter on the ground side but would I put two leads on the other side of the shunt back to the batteries or just a single lead.

SmartShunt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
harold avatar image
harold answered ·

You only use 1 + and - connection, you have 1 set of 12V


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

@mercman

Yes.

Nothing can be connected between the shunt and the batteries to meter properly.

I can see why you would ask that with the setup. Normal banks have only one take off point on both negative and positive. Usually at opposite ends of the bank.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.