EasySolar/ Multiplus 48/3000 Power generator issues.

Hello,

I would like to ask if this is normal that after i have generator connected bulbs on my inverter every 60sec changes from;

'Charger: Mains ON/ Bulk ' to 'Inverter: Inverter On'


I would like to ask someone to correct me as well if my configuration is not correct.

I cannot upload file so i give link;

https://easyupload.io/eqjbld


I would like to set up generator to start when batteries hits 50/55% so it can charge bats a bit.



EDIT:
SOLVED/ UPS MODE AS MANUAL SAID IN MY CASE MUST BE OFF. WEAK AC OPTION HELPS AS WELL


Generator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
basil katakuzinos avatar image
basil katakuzinos answered ·

Try turning off UPS function and see if the result improves

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

magicmike avatar image magicmike commented ·

Looks like it runs only under 'weak ac' mode :)

and yes- UPS function must be off.