I would like to ask if this is normal that after i have generator connected bulbs on my inverter every 60sec changes from;
'Charger: Mains ON/ Bulk ' to 'Inverter: Inverter On'
I would like to ask someone to correct me as well if my configuration is not correct.
I cannot upload file so i give link;
I would like to set up generator to start when batteries hits 50/55% so it can charge bats a bit.
EDIT:
SOLVED/ UPS MODE AS MANUAL SAID IN MY CASE MUST BE OFF. WEAK AC OPTION HELPS AS WELL