Switch Quattro on / off over Modbus TCP

Helo,

is there a way to switch the quattro off ans on over modbus?

I tried to read the state over address 3126 with unit id's 246 and 100:

com.victronenergy.inverter Inverter on/off/eco 3126


but it didn't work.

Any Ideas?


Thanks

Peter


Modbus TCP
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

How about if you use unit ID 246 and register 33.

1631133842313.png



1631133842313.png (18.8 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ganderpe avatar image ganderpe commented ·
Helo wkirby!

thanks for your answer!

I've read ID 246 register 33 already to get an idea what it's about.

I think this is represinting the Mechanical switch on the Quattro.

When i switch this mech. switch to of, the whole power in the house is off :-(

Actually I'd like to switch the grid only to off.

Because I have an intermitting error (grid feed from the battery), about every month or two, which tries to empty my battery :-(

When this happens (power > 500W to the grid at the same and time power > 500W from the battery for longer then 2 minutes) i'm sending an email to myself do an action.

This works fine, but I'd like to have it automated e.g. switching the grid to off for 10 seconds and then to on again, thats what I do to prevent draining the battery completely to the grid.

The best would be, if this problem was finaly solved... but ...........

Have a nice day!


Peter



0 Likes 0 ·