Helo,
is there a way to switch the quattro off ans on over modbus?
I tried to read the state over address 3126 with unit id's 246 and 100:
com.victronenergy.inverter | Inverter on/off/eco | 3126 |
but it didn't work.
Any Ideas?
Thanks
Peter
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Helo,
is there a way to switch the quattro off ans on over modbus?
I tried to read the state over address 3126 with unit id's 246 and 100:
com.victronenergy.inverter | Inverter on/off/eco | 3126 |
but it didn't work.
Any Ideas?
Thanks
Peter
How about if you use unit ID 246 and register 33.
thanks for your answer!
I've read ID 246 register 33 already to get an idea what it's about.
I think this is represinting the Mechanical switch on the Quattro.
When i switch this mech. switch to of, the whole power in the house is off :-(
Actually I'd like to switch the grid only to off.
Because I have an intermitting error (grid feed from the battery), about every month or two, which tries to empty my battery :-(
When this happens (power > 500W to the grid at the same and time power > 500W from the battery for longer then 2 minutes) i'm sending an email to myself do an action.
This works fine, but I'd like to have it automated e.g. switching the grid to off for 10 seconds and then to on again, thats what I do to prevent draining the battery completely to the grid.
The best would be, if this problem was finaly solved... but ...........
Have a nice day!
Peter