Multiplus II with Grid Connection and Gen with ATS

Is it possible to connect an ATS into "AC In" on the Multiplus II that switches to genset when there is a power outage and have the GX device know that it can not export any power as it has changed to Genset instead of Grid?

Or is there a better way of having Gen backup on a grid connected ESS system?

Multiplus-IIGenerator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
basil katakuzinos avatar image
basil katakuzinos answered ·

AC input types are basically static (Input 1 should either always be a generator or always be a grid). The best way to do this wouldbe to use a Quattro as it designed for two AC inputs and use with both grid and generator.

You can get away with this in a MP II but will probably end up having to do the changes manually every time you swictch from grid to gen (not ideal).

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

offgridvoltage avatar image
offgridvoltage answered ·

Good question Ross. Theoretically the MPII should see the gen output as grid (after the initial grid fail depending on ATS delay) and sync accordingly, then keep doing whatever ESS it’s setup to do. But in reality it depends on the generator. If it’s a high end full inverter 9kVA Full Sine Wave then all would be normal. But… if it’s a cheap Chinese Industrial grade genset, then it’s output would be a dirty square wave that swings between 48-52 hertz with voltage bouncing around. This output would rejected by the MPII as “week AC” and treated as a continued failed grid / LOM event and the MPII would just remain in anti-island mode. The only way around this is to disable "LOM" detection in the Grid Code VE_Config. Type "B" LOM Detection should still work fine with a decent stable generator. The perfect solution is to install a Quattro and therefore have a dedicated Generator AC Input AND a Grid AC Input.....

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image
Kevin Windrem answered ·

I have written an enhancement for adding an automatic transfer switch ahead of a Multi:

https://github.com/kwindrem/ExtTransferSwitch

This uses a digital input to tell the GX device if the incoming power is grid/shore or generator. The GX device then changes the input type from grid/shore to generator and sets the AC input current limit to appropriate values.

I can not speak to what happens with ESS feed-in when on generator. Does an input type of Generator disable feed-in? If not, additional work would be needed in ExtTtransferSwitch and I'd need help from someone who understands ESS to make sure power is not fed back to the generator.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

offgridvoltage avatar image offgridvoltage commented ·
Thanks Kevin. slightly off-topic, but would having an external ATS negate the need for LOM detection in Grid Codes ? I'm thinking that once the ATS is activated, there is physically an air gap between the grid and the rest of the loads / MCB / micro grid / PV setup etc etc. So it's literally a perfect ani-island measure.
0 Likes 0 ·
Kevin Windrem avatar image Kevin Windrem offgridvoltage commented ·
I'm no export on grid connection requirements but I'd say no you still need LOM. Some ATS won't transfer to the generator until generator power is present.
1 Like 1 ·
Show more comments
albertoot avatar image
albertoot answered ·

Hola. Yo necesito algo así y no encuentro solución. Pero tengo otra duda… ¿sería posible conectar un generador en AC OUT 1? Sería algo similar a lo que propone Victron en este esquema, pero sumando un generador

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image Kevin Windrem commented ·
NO.

The Multi and Quattro AC inputs disconnect from the inverter/charger core via a relay similar to the one on the AC output but the logic to control the input relays is completely different. The Multi/Quattro has circuitry that monitors the AC input(s) for voltage and frequency with the relay open. The inverter/charger core then attempts to synchronize to the selected input (AC 1 priority in a Quattro). Only after the synchronization is successful does the relay close.

The AC 2 output has no voltage and frequency monitoring so it is not possible for the inveter/charger to synchronize to it before closing the relay. Closing the AC 2 output relay would then connect out of phase, frequency and voltage sources together (inverter/charger core and generator). Extremely high currents would flow and certain damage to the Multi and generator would result.

1 Like 1 ·