helios-harvester asked

Phoenix Inverter 24V 1200VA 230V Does not follow lowest voltage cut-off

Dear All ,

I have a peculiar issue that the inverter even with hard coded lower voltage cut-off at 18.7V
and alarm at 20V ( Via VictronConnect and latest FW )

and still the inverter cuts off at 24 V exactly.

The current shunt and MPPT controller reports the same voltage during the shutdown

I hope someone could provide some light ?

Thank you


The Harvester

VRMMPPT SmartSolarPhoenix InverterVictronConnectVE.Direct
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

What voltage is shown in the inverter via VictronConnect?
What load is running at that moment?
Can you measure the voltage at the battery terminals of the inverter?

What wire gauge is used from the inverter to the battery and how long are the wires?

My guess is a high voltage drop due to a loose connection somewhere or to thin/to long wires.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

helios-harvester avatar image
helios-harvester answered ·

Dear @Matthias Lange - DE

Now the Inverter is under "Full" load : (138VA)
and I see on the Current shunt battery voltage 27.17V
and on the inverter battery voltage 27.11V
so 0.06V voltage drop from Shunt to inverter.
I consider this normal.

Any other insides ?

Thank you in advance

The Harvester

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

av1um avatar image
av1um answered ·

what kind of BMS are you using?
because, the detected values of the BMS will always count in the end (LTP).
if you are using a BMS which is configured seperately - by software or DIPswitch etc... - those hard coded parameters will overwrite any fixed parameter which you have set in the ColorControl / (even in the inverter itself) or whatever you are using for display / control.


example: assuming you have set a value for charging up to 27.6V in your inverter but you have set the BMS to start balancing at 3.6V for each cell, your MAX charge voltage will rise up to 28.8V before the system will enter absorption mode - 3.6V x 8 (in a 8S system).
the same will happen with battery low voltage: if you have set a parameter in the BMS to cut-off the batteries at 2.8V or lower, the system will continue to discharge until 22.4V

in your case the parameters might be set to around 3V / cell - that at least would explain the 24V cut-off.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

helios-harvester avatar image
helios-harvester answered ·

Dear All

@Matthias Lange - DE


I woke up today at around 5am the inverter was off on alarm. I started it and voltage didn't drop lower than 24v from the victronconnet and then re-alarmed and stopped.


So there is something wrong with the inverter FW. (its on the latest version) i will try to rollback 1 version.



Please advice how to move forward?

Thanks

The Harvester