Simple question.
Should the SOC% match the bar graph in the bottom RH corner of the gauge?
Ie, 3 bars = 60%, 5 bars = 100%
I believe the bar graph is probably correct & my SOC % is not for some reason.
I don't have BT so can't screen shot settings.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
It is linked to the setting 16. SOC relay (discharge floor).
Full = 100% and empty = you reached the SOC set in setting 16.
#16 setting is 85%.
Currently SOC is reading 91.9% & bar gauge showing 2 bars so assume 40%.
Additional resources still need to be added for this topic
26 People are following this question.