Is there any Configuration that I can add a remote switch for on/off/charge only for my two in parallel Multi Plus Inverters with a CCGX?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Is there any Configuration that I can add a remote switch for on/off/charge only for my two in parallel Multi Plus Inverters with a CCGX?
I could be wrong but from my understanding those settings can only be controlled by the switch on the units. Is their a reason you need to do this? allot can be configured while the unit is ON from VRM through the remote terminal.
Multiplus 12 / 3000 120-60
1.67 amp’s each 2 in parallel when on inverter mode no load.
= 80.0 amp/hr per day. = 10% of my usable 1000 lithium amp/hr house battery bank. With these inverters are off when not needed, my 1280 watt solar can maintain my usage.
It can be switched via the CCGX screen..
Or if you have a compatible MFD on the bridge, via the MFD App.. https://www.victronenergy.com/media/pg/Venus_GX/en/marine-mfd-integration-by-app.html
I'm not sure why you switch to charger only when on shore power. When fully ON it will passthrough shore power to loads, and charge with any remaining shore up to the limit you've set on shore. Multis cannot invert and charge at the same time, so you can't deplete your batts unless loads exceed the shore limit.