Would anyone know why the SOC synchronisations are zero?

This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi ,
Would anyone know why the SOC synchronisations are zero?
Looks like a new system so how should there be some synchronizations counted?
A synchronization is counted after the SOC drops below 90% and goes up to 100% again.
thank you - I did not see that in the documentation about the SOC dropping below 90%
It is in the manual at chapter 5.5.
https://www.victronenergy.com/media/pg/SmartShunt/en/operation.html#UUID-fb41551c-8916-9f71-17bf-259a7fee2012