Hi All,
I am currently running a Multiplus 2 3KW connected to a 15S65P 18650 base battery. My BMS is Batrium WM4 that talks over CANBUS to a Rpi4 running Venus OS. Im using a CT clamp to mains to try and keep the grid value at 0W. Set in link below.
https://community.victronenergy.com/questions/32828/can-current-transformer-replace-energy-meter.html
Everything has been running sweet as a nut for the last 18 months but there is one issue that I cannot appear to get to the bottom of and that is the power limit of the system. The intention was to never run it more than 1000W.
The issue I have is when a big load is switch on in the house such as a kettle, cooker heating element or iron. The inverter rams up to max invert of 3kw and then slowly ramps back down to 1000W. So it appears the power limit works but the inrush current of 50 to 60 Amps is something I want eliminate.
In the manual section 4.3.9. The manual states this:
The losses in the inverter/charger are not taken into account. If you want to limit the amount of power being drawn from the battery, you will have to set this limit slightly lower to compensate for those losses.
Power coming from the MPPTs is not taken into account. Using this feature in a system with MPPTs can cause the output power from the MPPT to be reduced.
This limit is with respect to power drawn from the battery and will affect the total of all phases.
This limit only applies while connected to AC-in: In inverter mode, the AC loads determine how much power is drawn from the battery.
BULLET POINT 1- Ihave tried setting the power limit to 700W but i sytill get a 50-60A inrush.
BULLET POINT 2- Im not using MPPT's.
BULLET POINT 3- N/A
BULLET POINT 4- I am only connected to AC IN using as a bidirectional inverter/charger. I have no loads connected to the AC out. When is sates 'inverter mode' does this mean this setting? inverter only? Or is there another setting?
I currently leave the switch in the ON position and do not run it 'inverter only'. This is because I want it to invert/charge when required.
Does anyone have any idea how I can limit it so it ramps up to 1000W when large loads are switched on? Or will I have to run mode 3 to eliminate this issues?
Any help would be much appreciated.
Thanks
Gareth