I have a single pylontech us3000c that is hooked up with a multiplus, blue solar mppt, and cerbo gx.
The system was initially ran for a couple days and then an alarm happened indicating an Internal Battery Failure. Upon troubleshooting I found that the DVCC was not turned on and the battery is at 54v. So I’m assuming it alarmed internal failure because of over voltage.
I changed the DVCC to on and adjusted the voltage to 52v, but the battery is still in alarm. Is there a way to discharge the battery while in alarm? The max charge and discharge rate has gone to 0A.