Generator start/stop wiring

Hey,

I'm trying to configure the auto-start/stop for my generator using a Cerbo GX.

The Generator starts with a (very common) 3-wire ATS plug. I've run a 12V +ve and -ve from a battery and spliced to my communication cable as directed here.

1628085605000.pngThe start/stop relay on the Cerbo is 3-wire (NC, NO, COM). Does anyone know how the ATS wiring and the Victron relay wiring marry up? I can't find any documentation online.


Cheers

Generatorauto gen start
1628085605000.png (52.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
tom-galletti avatar image
tom-galletti answered ·

I've managed to answer this myself purely by chance, so will update here in case it helps anyone else:


on the ATS end:

1 -> live wire

2 -> neutral wire

3 -> earth wire


on the Victron end:

live -> NC

earth -> COM

neutral -> NO


Note - on my Hyundai, you must NOT run 12V through the neutral and live wires (despite what the ATS diagram says) or the gen won't start.

You must also make sure the ignition is set to OFF, or the gen won't start.


Hope this helps someone else.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nesswill avatar image
nesswill answered ·

Hi, would this work with my Genny

It's a DHY18KSEm controlled by a MRS10.

Thank you, Dave.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic

MultiPlus Generator FAQ

GX - Generator auto start/stop

Automatic Generator start/stop

 Hybrid Generators

Virtual switch - Generator start/stop

Additional resources still need to be added for this topic