Rainy day AC load support

Hi is there a way to set EES to not charge the battery on rainy days and only support the grid?


1628082700155.png

On my settup its allways slowly charge the battere to the threshold and then switching completly to battery until its empty again. But it would make more sense if the battery would stay at 80 to 90% and the 230 watts would support the AC loads. Thanks for your help

ESS
1628082700155.png (142.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@MrYoshii

Lower your SOC in case of grid faliure percentage in the ess menu on the gx device

Or (depending on your batteries in your system) you can switch of the battery life option. Then the system will not prioritise the battery charge to 100%.

https://www.victronenergy.com/media/pg/Energy_Storage_System/en/configuration.html#UUID-44102771-a07a-55eb-b676-772c0d78e5fa.

https://www.victronenergy.com/media/pg/Energy_Storage_System/en/controlling-depth-of-discharge.html#UUID-af4a7478-4b75-68ac-cf3c-16c381335d1e