Is it safe to turn off a MultiPlus under load via VRM?

I have a MultiPlus 24/2000/50 connected to a VenusOS device which allows me to connect to it via VRM.

About the only thing I will be using with the inverter is a small air conditioner that uses 420W while the compressor is on.

Is it safe to connect to VRM and tell it to turn off my inverter while the A/C is running? This is just incase I end up being away from the trailer unexpectedly for a few hours and realize I left the A/C on.

MultiPlus Quattro Inverter ChargerVRM
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Kevin Windrem avatar image
Kevin Windrem answered ·

Should be fine. The shutdowns appear to be very clean even under heavy load.

Just wait about 5 minutes to turn it back on to avoid the huge power spike when the compressor tries to start while there's still pressure in the tubes.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rmaddy avatar image rmaddy commented ·
Thanks. I will rarely need to do this but hopefully it's fine if the need arises.