question

pau-hana avatar image
pau-hana asked

AC input to Quattro from generator

Good evening. I tested my generator output prior to connecting to the Quattro AC1 input. Generator output is 120v 60hz. Some questions:

- checking ground with either hot or neutral resulted in a reading of 55-60 volts AC.
- Connecting neutral to hot resulted in 120v.


So, is this safe to connect to the Quattro as is?

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@Pau Hana

No. You have a floating neutral. The ground relay will `possibly fry in the inverter.

They are not safe in general to use.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pau-hana avatar image
pau-hana answered ·

Thank you- what is the solution for the floating neutral?

2 |3000