Hi There Everyone,
i have read a few posts with some differing answers, but would love to see that you guys think on this subject
I currently have two 400w Panels feeding a 100/50 controller running 12v charging two 200AH AGM batteries in Series. the specs of the panels are open circuit voltage at 49.1V, and short circuit current at 10.10 Amps
the load is 10amps constant at night, and during the day goes back to grid using a ATS, so the batteries have no load charging during the day.
now that winter is here if finding after two days my batteries are drained, due to no sun, clouds and also a tree in the way for 2-3 hours of sun.
I'm thinking of adding another two of the same panels to the system, and wiring them series-parallel, so i keep the voltage under 100v but increase the amps. now i know this should be ok in winter as it wont get to the 50 amp limit of the controller, but summer would be a different story.
i can see on the 100/50 datasheet that nominal power is 700w, (i currently have max 800) but if i do this the system will be at 1600w. i can see that is says Max. PV short circuit current is 60 amps, so i know i will be under this value, and i don't mind if i am not using the panels full capacity in the summer, but i know ill have more power being generated in the winter
what are all your thoughts on this? as getting another 100/50 would be costly, and if needed i would go to this direction, but seeing that I'm not going over the specs of the controller, i can see an issue why this would not work, unless people have other experiences
Thanks again for you time to read this and welcome and input