Is there a rule between PV size on Solar chargers and the inverter/charger?

For example, I have a system of 6 Quattro 15 KVA and 19 MPPT Rs 200 A.


offgriddc system
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
shaneyake avatar image
shaneyake answered ·

No, you can have as big of a DC array as you would like. The only thing that has to be sized correctly is that you charge controllers don't exceed the batteries max charge current. This could mean just setting the limits lower on the charge controllers or having a battery with CAN BMS which can adjust the charge rate.

So PV and Battery should match but inverters have no effect in DC coupling.