question

Kasper avatar image
Kasper asked

Quattro 24/8000 current limt.

I have a Quattro 24/8000KVA and the current limt cant go under 10 Amps like the 5000KVA cant go down to 4 Amps. in scandinavia we often have problems with not being able to get more than 6 - 8 A out of the shore power. how can i come down under 10 A limit current ind the Inverter? anyone know if it is possible to get a special firmware from Victron ?

MultiPlus Quattro Inverter Chargerfirmware updatecharge current limitcurrent limit
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Mike Dorsett avatar image
Mike Dorsett answered ·

In this case, I would use a smaller charger unit to charge the house bank, while the Quatro remains in invert mode. Then you can control your input current to a lower level.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.