I'm running two MulitPlus 24/3000/70-50 120V in parallel. firmware v482.
When the multis inverting the AC-OUT Watts is close enough (+- a few percent) to V*A = W.
With Honda EU2200i generator running:
AC IN: rough average V*(A*1.6) = W
AC OUT: rough average V*(A*2.56) = W
Input limit: 5.0A
Overruled by remote: Off
Inverter Power Assist: Off
With generator running
AC IN 1:
Voltage: 120
Current: 9.5 (15.2\9.5=1.6)
Power: 1826W
Frequency: 60.3Hz
AC OUT L1:
Voltage: 120
Current: 3.8A (9.725\3.8)=2.56)
Power: 1167W
Frequency: 59.9Hz
Battery:
Voltage: 26.69V
Current: 22A
As long as I set the Input limit to 1/3 of what I want the maximum watts pulled from the generator, it won't overload the generator. Setting it at 4.3A in general ensures it never pulls much more than 1,800W. At 5W it will creap up towards 1,900W and bounce between there and 2,100W at 120V.
I did measure same length 5' (1.5M) and torque down the 6 AWG(13.3mm2) THHN copper from busbar to the two Multi's the same. However, amp meter shows load is different about 1:3 between the two Multi's. Wondering if that mismatch in load is the cause of my issues? Unsure what to do other than maybe change out the THHN wire to Ancor Marine 266 strand tin coated copper.
Just so strange that the AC OUT L1 current is so far off when in passthru vs. inverting.
Thanks in advance for any ideas.